Current Sensing
The current in the mains supply is measured by placing a current sensing resistor in series with in this case the neutral wire. A current sensing resistor is a low resistance resistor with a high power rating. When current flows through a resistor there is a voltage drop across it: Ohms Law. This voltage is what is measured. The current sensing resistor looks like this:
The important design considerations here is what size current sensing resistor you need, a few values determine the size of the current sensing resistor you should go for:
  • The maximum peak power you want to measure.
  • The input voltage range of the isolators, -0.256 to +0.256 for the HCPL-7520.
  • Power rating of the resistor.
The peak power can be a lot higher than the average power for example a lamp is rated at 60W will actually have a peak power of 120W and a laptop rated at 60W due to its switched mode power supply will have a peak power of many hundred watts.
Lets say we want to be able to measure a peak power of 3000W.
First we find the max peak current that gives us a peak power of 3000W:
Now that we have our peak current we use the value for the isolator voltage input range to find the ideal value for our resistor. Using Ohms Law:
The power dissipated in the resistor is given by:
The Power rating of the resistor should be a bit above this value. We then head over to farnells Ohmite current sensing resistor page to find a suitable resistor that fits these values: Farnel's Ohmite range
The Ohmite 13FR025E is the closest match it has a resistance of 0.025Ohms and therefore will allow us to measure a larger peak current value and therfore a larger peak power value.
The power dissipated in the resistor at this current:
This power is lower than the 3W rating of the resistor and so a 3W resistor would be fine, we could always go for the 5W resistor just to be safe. The peak power we can measure:
Therefore we can come to the conclusion that a 0.025Ohm 3W current sensing resistor such as the Ohmite 13FR025E is a good choice for our needs.
What modification should be
What modification should be performed to measure the alternating current in the line alive?
Gracias!!
Hey Alf, the current in the
Hey Alf, the current in the live is the same as the current in the neutral, so no change is needed.